[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: Discuss Comments on Sht A6 & A7 (fwd)
Hi Eric,
Thanks for all you careful comments.
We passed on all your comments to Rebecca, and we went over them
yesterday. Below are some notes of my own:
Cheers, Elton.
Elton Smith
Jefferson Lab
elton@jlab.org
(757) 269-7625
On Sat, 25 Mar 2006, Eric Scott wrote:
> Hi Elton,
>
> C2:
>
> Strikes me as odd that the closes fire hydrant to Hall D (NE of the
> hall next to the fence) is about 120' from the nearest paved surface and
> about 225' from the building.
>
Fire code requirements will be verified by HSMM
>
>
> A6:
>
> Are we sure that the beam dump cooling skids will not overheat
> the tagger area?
The heat exchanger should not add any heat load to the area, simply
extract it into the chilled water system.
>
> Why is there 42' 8" from the US end of the permanent magnet to
> the wall, isn't half of this wasted space?
This is to make sure that in the accidental dumping of the beam it
sufficiently clears the beampipe. Take a look at GlueX-doc-599.
>
> I thought we decided that we did not need the dumbwaiter into
> the tagger.
Indeed, however, Rebecca is leaving it in for now. Accelerator has seen
the benefits of using it for their maintenance needs.
>
> A7:
>
> I still think that the dumbwaiter needs to move south so that its
> back wall is even with the bottom of the stairs.
I think either way it is positioned, it cannot be both at the top and
bottom of the stairs. However, Rebecca will add a question about location
and also about adding a landing, but this might complicate the geometry
further.
>
> Does the Gas Shed need a penetration into Hall D?
>
Penetrations are needed, but won't be indicated until beyond 35% design.
> It would cut down on water usage if a urinal was added to the
> bathroom.
Unisex bathrooms usually do not have urinals.
>
> Any way we can get the 12'-3" X 8'-11" notch made into a work
> station space? Seems a waste.
>
Yes, also the tel/comm. room is likely too small and should not have the
entrance from the rack room. We will ask them to move it to and perhaps
expand using the "wasted space".
> Cheers,
>
> Eric
>
> Elton Smith wrote:
>
> >HI Eric and Richard,
> >
> >You can find the three revised civil drawings at
> >http://www.jlab.org/Hall-D/civil/drawings/design35/Revised_C2_%20A6_A7
> >
> >Let me know if you have any comments by Monday evening so that I can pass
> >these on to Rebecca. She has asked me to give comments by Tuesday.
> >
> >Thanks, Elton.
> >
> >Elton Smith
> >Jefferson Lab
> >elton@jlab.org
> >(757) 269-7625
> >
> >---------- Forwarded message ----------
> >Date: Fri, 24 Mar 2006 17:00:14 -0500
> >From: Rebecca Yasky <ryasky@jlab.org>
> >To: Elton Smith <elton@jlab.org>
> >Subject: Re: Discuss Comments on Sht A6 & A7
> >
> >Elton,
> >Here is the pdf of the three revised drawings. They are half-size
> >drawings - 11" x 17".
> >Rebecca
> >
> >
>